OPC Siemens ----> OPC Delta V 14.3.1

Hello.
In version 12.3.1 of deltaV I had installed opc mirror with connection to opc siemens Wincc with the administrator user.
Now that I update to version 14.3.1 opc mirror cannot find the siemens opc.
I already created a windows session with the administrator credentials in the siemens workstations, from the siemens OS1 the OPC DeltaV was observed but from the application the siemens opc is not observed.

1-Sorry for my English
2-Somebody could help me?

Thanks

1 Reply

  • Could it be a COM / DCOM setting on the APP station? From "OPC Mirror Tips" in help,
    "OPC Mirror does not use DeltaV security . . . you must have the proper COM authentication credentials to connect to OPC Servers and define data mapping"
    Also - DCOM - might be a factor if OPC is not running on a DeltaV node?