How ICSS DeltaV OPC Server (Historian Server) to get the data from ICSS Siemens OPC Server

How ICSS DeltaV OPC Server (Historian Server) to get the data from ICSS Siemens OPC Server?

At a platform, ICSS Siemens OPC Server get data of three package: Metering, Slug Catcher, Gas Compressor.

We are at another platform, ICSS DeltaV OPC Server (Historian Server ) need to get the data of 3 that packages.

Two OPC Server at two platform connect together through Digital MicroWave.

Please advise what and how to configure and setup so that 2 servers work together.

Thank a lot.

  • In reply to ngovankhoi:

    Regarding OPC DCOM, Firewalls and ports, I would take a look at this:
    techsupport.osisoft.com/.../2973OSI8
    Because of the ephemeral ports principle of OPC DCOM, the range of potential ports is too wide to open all up, but you can limit DCOM port selection per a referenced Microsoft article.
    If you are using windows firewall, then I believe specification of the applications on both sides should work, but if it is a third firewall in between the server/client, you probably cannot, hence the reliance on tunneling applications like Matrikon's.

    OPC mirror does not handle OPC HDA data, if that's what your question "Does OPC Mirror support for transfer Historian?" refers to.