Hi,
I am trying to establish Delta V OPC redundncy but due to some error it is not done.
I have done as per the Delta V Books on line , even 1 machine has become active and other as standby , but still redundancy is bad.
I have attached snap shot of the error that comes up while running configuration file.
Kindly share if any body has ever faced the issue or how can i be sucessful in configuring the OPC Redundant server.
(For info: i have two physical machines and i have selected redundant application station in explorer and loaded the license also)
Regards
Sumit D.
In reply to bobgally:
The issue is solved.
It was due to *.ini being deleted from EWS and auto-update disabled for OPCDA.
Also, latest 11.3.1 hotfixes were installed