I would like to estabilish a communication between DeltaV Profibus card and Siemens Simatec ET 200M PB device.
Do you know any guideline how to do the configuration? I know that in some cases one IO slot in ET 200M is not the same as slots in the DeltaV Profibus Card (we need to add dummy slots and so).
Thanks for the answer,
Gabor
Best regards.
Butler faith.
First of all you need to have the right GSD file as pointed out allready.
Then you can add the device(s) under your Profibus port.
Based on the configuration of I/O modules in the ET-200 device you can add the Profibus Slots under your device. Please note that the Slots must match the modules in the ET-200 device exactly! For an ET 200M (IM153) the first three slots must be configured with Config for Slot1, Config for Slot2 and Config for Slot3. For empty positions in the ET-200 device DUMMY slots must be inserted in the Profibus Slot assignment. See example in below pciture.