We have an existing MODBUS TCPIP segment with a number of Slave MODBUS TCPIP devices on that segment. We have one VIM2 card connected below an existing DeltaV controller acting as a master device communicating with those existing slave nodes. All is well and working.
We have a VIMNET programming workstation connected to that segment. See the image below for the current arrangement shown as items outlined in blue.
We are adding a further DeltaV controller to the system and wish to add further MODBUS TCPIP devices to communicate directly with that new controller through a new VIM2 card, see items outlined in orange.
We DO NOT require the existing VIM2 node to communicate with the new slave devices, and we DO NOT require the new VIM2 node to communicate with the existing slave devices. The existing and new MASTER/SLAVE relationships are logically separate and will remain that way.
We would like to retain a common physical TCPIP segment and address range, allowing us to retain our existing single programming workstation and VIMNET explorer. The diagram shows our proposed and desired arrangement.
My understanding is that the MODBUS TCPIP protocol does allow multiple masters on an IP segment (unlike traditional MODBUS RTU)
So the questions are.
1. Does the VIM2 with the IOD-4111 - MODBUS TCP IP DRIVER FOR DELTAV VIM2 support this arrangement?
2. Does anybody have experience of using this arrangement?,
3. Are there any concerns / tips / contraints?
The alternative would be to have a totally new separate physical IP segment and switch and a second VIMNET programming workstation.
Many thanks,
In reply to Jake Nichelson:
Thanks Jake, I understood MODBUS TCPIP allowed it, just wanted to know there were any limitations with the VIM2 implementation that prevented it, such as fixed IP address (for itself) or anything odd like that. Regards
In reply to IntuitiveNeil:
In reply to lazy_engineer:
In reply to Lun.Raznik:
Thanks, and I'm corrected on my terminology "clients" and "servers" now not the old RTU term "masters" and "slaves" A subtle change but I guess it brings me into to 2000's
On Thursday, July 9, 2020, 1:05 AM, Lun.Raznik <bounce-LunRaznik@emersonexchange365.com> wrote:
Update from Emerson Exchange 365 Lun.Raznik Have you tried this link? emersonexchange365.com/.../ Try to disable all notificaitons. View online You received this notification because you subscribed to the forum. To unsubscribe from only this thread, go here. Flag this post as spam/abuse.
Have you tried this link? emersonexchange365.com/.../ Try to disable all notificaitons.
View online
You received this notification because you subscribed to the forum. To unsubscribe from only this thread, go here.
Flag this post as spam/abuse.