DCC Interlock state

I_STATE1 won't use the correct named set. I have both my I_STATEn set to a custom named set. Only the second one I_STATE2 is being shown correctly.  

5 Replies

  • In addition, when I create a new interlock, if i set I_STATEn to a different state ( for instance set it to State 1) then download it does not show the new state as the On-line value. It's ass if that Default database value doesn't get downloaded, so the online value stays as what it was. If I change it online, then it continues to work even after subsequent downloads.
  • In reply to TreyB:

    What version are you running? Originally these were set to be copy critical meaning that they wouldn't be updated on a download but a hot fix was released to change this behavior which is described and can be downloaded in the KBA AK-1500-0067.
  • In reply to Matt Stoner:

    v14.3.0

    I'll look into the Hotfix, thanks.
  • In reply to TreyB:

    Hotfix was for v13 so I'm wondering if this is a real controller, virtual controller or a workstation that the module is running in?

    If real controller is it flashed to v14.3?
  • In reply to Matt Stoner:

    yes, controller 14.3.0.6984