Now that DCC/EDC blocks exist. Should I use the DC/CND block combination for Discrete Control?
Do I need to take Controller Loading into consideration?
Does the new DCC/EDC blocks reduce controller loading or increase controller loading compared to the DC/CND blocks?
Does anyone have any comments or experiences they would like to share?
Andre Dicaire
In reply to ShawnHakim:
Just keep in mind that using the DCC with a DC block will have some limited functionality as only Interlocks and Permissives will be possible in a "standard" method.
The DC block can only interlock to the Passive state (defined by named set 0 value) while the DCC supports Interlocking to any state.
All the DCC Permissive functionality (Permit or Prevent) can be used with DC.
The DCC Force Setpoint functionality can NOT be used with DC unless some special logic is created in addition to the DC and DCC blocks.