Changing default Administrator account password in a workgroup environment

Hello everyone, I'm considering changing the default Administrator account password in the Delta V system that we have installed in our site for security reasons. We are in a workgroup environment; I know that this arrangement is not recommended and I am already considering going back to a domain, but in the meantime I hope you guys can help me with this. I know that I should set the password to be the same on every computer because doing otherwise may create conflict in some services, but is there anything else that I should be worried about before making the change?

Many thanks for your invaluable help.

  • Do not change the password using anything except the DeltaV Workstation config or the setpass utility. This will ensure that all services are running and with the correct credentials after the change. The only other thing to worry about is any third party applications that access data from DeltaV (OPC, PI and Others) If you have installed these they may be configured with the DeltaVAdmin account and then would have to be updated also.

    This was discussed here also. 

    Here is the information from the v 10.3 BOL article on Deltav system security: "The DeltaVAdmin password is pre-assigned in your DeltaV system. This password should be changed after you receive your DeltaV…

  • To clarify, are you talking about DeltaVAdmin or Administrator? As noted, there may be dependencies, specific to your system, that require that account. Checking the Services console and your DCOM configuration are a good start.

    If you're referring to Administrator, this account is disabled in DeltaV 13.x and above. If you are targeting these versions, it would be a good idea to transition any services using Administrator to a dedicated, non-managed service account.
  • In reply to Ray Emerson:

    Thanks Steve and Ray. I should have clarified that I am on v11.3.1 and I am talking about the Administrator account (I'm not really sure that there is a DeltaVAdmin on this version). Just changing this default account's password using the Delta V User Manager and making sure that the new password is the same for all computers in the workgroup wouldn't work?
  • In reply to DXSANCH:

    Oh, I've noticed now that the DeltaVAdmin service account is there, even though not visible from the Delta V User Manager. In any case, and as I said before, that's not the account I ment, but the Administrator account instead. Thanks for your help!
  • In reply to DXSANCH:

    DXSANCH, the Windows built-in Administrator account should be disabled completely and replaced by another username as already mentioned by other DeltaV users on this thread - and yes, since you are in a workgroup environment you will need to do that on every station of your system - domains would not only make this process easier, but also improve the overall cybersecurity of your system.

    As also said, since v13+ systems already force users to define the username of an administrative account, and we also have the DeltaV Security Administration tool in v13.3+ that makes it simple to go through the process after an upgrade to v13. Instead of managing this account, you should really disable it altogether and then manage its replacement accordingly.

    Worth noting that an upgrade to a newer DeltaV version will improve the cybersecurity of your system from various angles.