I have recently hooked up a 3051 pressure transmitter to our delta v (rev13.3) test rack and recorded base line readings and calibration verification into AMS (13.5) and everything worked as expected.
Once complete the E/I technician powered down disconnected the analog wiring from the device prior to disabling the HART channel and deleting the tag from the test rack controller.
The same tag was then installing out in the process area under a new controller and the 4-20ma signal (percent field value )is being used and working in the module.
The channel is HART enabled and the device was auto sensed & the proper device and revision was identified, on the channel. Once I went into AMS and tried to scan that particular device and alert came up stating that AMS could not communicate with the device.
We could go out to the device and hook up to it with a 475 with no problem and configure the device locally.
My question is, why can’t I communicate with the device via AMS?
Is there a particular order to follow while setting up a HART device on a test rack, decommissioning it and the re commissioning it on a different controller.
thanks for your feedback in advance
In reply to Dan Mos:
Update from Emerson Exchange 365 <4TSEJO475AEY-jpg_2D00_70x70x2-jpg> Tinh Phan Hi Dan, since you have commissioned this device on a different channel on a different controller then decommissioned it and then move it to another DeltaV channel using the same Device tag. I believe that AMS DM is still looking at the same path as when you first commissioned the device and this is why AMS can’t communicate to the device since the path is not there anymore. I suggest you go to the first channel the device was on and change the DST back to its original dst and make it non HART channel (don’t forget to download) then use AMS DM remove device utility and remove that device tag from AMS database. Autosense the Device again from its current connection then do a rebuilt Hierarchy in AMS DM. This should do the trick. If it don’t, let me know and we can chat to figure this out. View online You received this notification because you subscribed to the forum. To unsubscribe from only this thread, go here. Flag this post as spam/abuse.
Hi Dan, since you have commissioned this device on a different channel on a different controller then decommissioned it and then move it to another DeltaV channel using the same Device tag. I believe that AMS DM is still looking at the same path as when you first commissioned the device and this is why AMS can’t communicate to the device since the path is not there anymore. I suggest you go to the first channel the device was on and change the DST back to its original dst and make it non HART channel (don’t forget to download) then use AMS DM remove device utility and remove that device tag from AMS database. Autosense the Device again from its current connection then do a rebuilt Hierarchy in AMS DM. This should do the trick. If it don’t, let me know and we can chat to figure this out.
View online
You received this notification because you subscribed to the forum. To unsubscribe from only this thread, go here.
Flag this post as spam/abuse.
In reply to Tinh Phan: