Hello guys,
I have a project which they demand me to do a prompt for valve faceplate (as picture below). Example for the operator prompt : " Do you wish to open / close this valve?".
Does anyone have an idea how to do? Still under training for Deltav 13.3
Thanks.
Best Regards
In reply to Ashwini.ruikar:
Ashwini is correct that the MsgBox function can be used for this.
My question would be why this is a requirement. I come accross this frequently where a well meaning design engineer adds this as a requirement and it really annoys the Operations folk.
When the are told its so the valve will not be opened accidenly. The response usually is I have to log onto the system, select the valve to open the faceplate, change the mode of the valve to AUTO and then click OPEN. Do I really have to confirm again that I want the valve open.