We are experiencing an issue with the I_DELAY_ON parameters in the new DCC block in Version 13 where the values configured in the database are not being passed to the controller. No matter what we change the value to in the database, when downloaded the online value remains at 0. Additionally, we can change the value in online mode and after being downloaded again, the parameters will hold on to the value they were changed to in online mode even while choosing not to upload the parameter values. I checked the download script in the powerup directory to verify that it contains the correct values configured in the database and it does. But it still is not getting passed to the controller. Note this is on a development system and we are using a SVIRTUAL controller.
Has anyone else experienced this problem?
Try checking the parameter download behaviour for your module.
One of the settings means it never takes the configured value. Cant recall which it is without looking but this behaviour is what you get
The smart switch modules have the parameter download behaviour set that way.