Hello.
We are using DV v14.3.1 with SIS functionality
Standard type of layout: ACN => SZ-CTRL => CSLS => LS Charms
The system is in production and fully running. Due to increasing Cyber Security efforts, we want to establish a - from our poinit of view - new routine to lock/unlock the installed SZ-CTRL and CSLS. For the CSLS part we want to use the software "lock"- functionality and the hardware "unlock inhibit key switch" on the CSLS-carrier as well. Therefore we have to active the "Enable Unock Inhibit Key Switch" setting in the Security-Tab at the properties-dialog of the CSLS in the DeltaV Explorer. After activation a download will be necessary.
The questions is: will the download and the changed properties influence the CRC-values (device, firmware or IO) or will they stay the same?
Thanks for your support!
Best regards, Stefan
Stefan Müllner Senior Plant Engineer - Automation & Systems
METADYNEA AUSTRIA GmbH
In reply to Sergio Diaz:
Just to illustrate what Sergio just mentioned
Before enabling Unlock Inhibit Key Switch and downloading the logic solver
After enabling Unlock Inhibit Key Switch and downloading the logic solver
Both overall control module CRC and LogicCRC also remain unchanged.
Rgs,