I am trying to integrate DeltaV OPC server with HIMA OPC server. Connection to both servers has been established as confirmed using the Watchit tool. But after creating a pipe i get the error message "Unable to browse server". Reading through a similar post on this forum, same problem was solved after registering some Dll files. I've done the registration yet the problem persist. I will appreciate if someone can assist on how to solve this problem.
Thank you
Hi Moizsawa,
is one of the servers a client, or are you trying a server to server connection?
"OPC HDA Client Connectivity
OPC HDA clients may be installed on the Application Station and connect locally to the DeltaV OPC History Server
or they may be installed on non-DeltaV workstations and connect remotely to the DeltaV OPC History Server. If an
OPC HDA client is installed on a non-DeltaV workstation, the DeltaV OPC client utility OPC Remote must be
installed on the non-DeltaV workstation. OPC Remote is required on the non-DeltaV workstation in order to
establish client connection to the DeltaV OPC History Server. Installing the OPC Remote utility on the non-DeltaV
workstation will create a DeltaV Admin account and install and register the appropriate OPC proxy/stub DLLs
required by the DeltaV OPC History Server. To install the OPC Remote utility, use the setup file located in the OPC
Remote directory on the DeltaV Installation DVD (Disk 1, DV_Extras\OPCRemote.exe). The version of OPC
Remote must be the same as the installed version of the DeltaV system software."
Niklas Flykt
Klinkmann Oy
nikfly@gmail.com
In reply to Niklas Flykt:
In reply to moizsawa:
In reply to tklatt: