DeltaV 11.3 OPC Server connection with third party OPC Client
Hello
I am in process of setting up OPC server on the DeltaV.
The target is to prepare DeltaV tags to be polled by remote non DeltaV OPC client/server.
I have applied licenses for: OPC Remote Sevices and OPC Server: 250 Data Values as well
1. After installation of OPC Mirror, I tried to open configuration utility, but it was proposed to pass registration procedure.
I have my license of Full Span of Control - does it mean OPC Mirror license comes within base license pack?
2. I also have installed OPC Services and Matrikon OPC Explorer(as alternative) on my virtual machine. When poll with OPC WatchIt - it`s OK, data
is shown correctly without any issues. But when try Matrikon OPC Explorer, message appears "No OPC Servers are installed on this remote machine \\[remote_machine_name]. Before
proceeding ensure that you have correctly installed an OPC Server".
Kindly advice what I could do wrong? Are there related documentation regarding this thread?
Thanks i advance, your assistance is appreciated
Daniyar Mamenov
Design & Application Engineer
Projects - ME&CIS
INTECH Process Automation - Kazakhstan Office
  • You indicate the third party OPC server is polling data FROM DeltaV, therefore, you need to setup that third party OPC server to POLL data from DeltaV. It seems you are trying to do two things in your explanation. I think you want to read data from DeltaV and receive to a remote OPC server, correct?
    OPC Mirror is what we use to read data from one OPC server (DeltaV or any third-party) and write to a second OPC server (DeltaV or any third-party). However, from the licenses you list if you do want OPC Mirror, you need an OPC mirror license, minimum 2 servers mirror license (one for DeltaV OPC server and one for your remote OPC server).
    Application station have 250 OPC points as standard, so why do you need a 250 OPC license? Are you using a normal workstation perhaps?
  • In reply to AdrianOffield:
    Correct
    I thought that I do not need any additional license, mean OPC Mirror License is part of base license for EWS, OWS etc
    License was proposed by local Emerson supplier...
    What you mean by "a normal workstation"? I`m using my ProPlus as engineering station.
    Daniyar Mamenov
    Projects - ME&CIS
  • In reply to Daniyar Mamenov:
    Normal workstation is Pro+, Operator Workstation, Pro station, basically non-application station.
    What DeltaV station are you trying to read OPC data from, the Pro+?
    OPC Mirror is not part of base unfortunately.
    FYI, you could use an alternative solution from either Matrikon or Kepware for brokering OPC data transfer between two servers. They have application that performs the same function as OPC mirror.
    Yes, it`s Pro+
    Could you suggest products of mentioned vendors as well.
    Ok, let`s assume I`ll buy OPC Mirror license for 2 servers. Still, I need Application Station for OPC data exchange?
    Thanks a lot, Adrian!
    Daniyar Mamenov
    Projects - ME&CIS
    If you have less than 250 points to transfer then the license you have is sufficient, you just need the OPC mirror license (2 servers), assign this to Pro+ and then configure OPC mirror to map data. (You'll need to make sure you have a common user account on both system!). No need for additional application station and licenses unless you are looking to transfer more than 250 points.
    Matrikon OPC Data Manager
    Kepware Linkmaster
    Hope that helps.
    There is also the Excel Addin license that you can apply to he Proplus whci will increase the OPC server license to 500 tags. If you need more, an Application station is needed and can be scaled up to 30250 tags.
  • Hello Daniyar,
    FYI if you have to transmit OPC data across Firewalls, you can use our OPC .NET developer toolkit to create your own client and access OPC data from DeltaV. This is an alternative to OPC Mirror and requires that you develop all the data mapping and processing. The good news is that you only need to license the points on the Application Station or ProPlus. You do not need an OPC Mirror license. Refer to the toolkit page here: www3.emersonprocess.com/.../
  • In reply to Brian Crandall:
    Brian Crandall said:
    Hello Daniyar,
    Noted with thanks!
    Daniyar Mamenov
    Projects - ME&CIS
  • Former Member
    Former Member
    Daniyar,
    From what I can gather you have installed and OPC client/server to read data from DeltaV on a virtual machine. If that's the case, have you set up your DCOM permissions correctly? Are the DeltaV server and virtual OPC server on the same domain? If not then you need to get your DCOM permissions absolutely spot on otherwise you won't get a connection (this includes having the same user on both machines, and setting up the launching user of the DeltaV OPC server with the correct permissions).
    We have setup an OPC connection to DeltaV, but to get round all the DCOM issues, we installed the OPC client on the same server as the DeltaV OPC server - no OPC mirror required. We then setup the OPC client to run under the same account as the OPC server so there would be no issues in account settings. If you then need to get your data out onto a separate network across firewalls, just setup a firewall rule that allows a point to point connection between your server and the machine which will be reading the data. I think you can even specify a set port for the traffic to be sent over which ties the firewall access down even further.
    I hope I have understood your current situation, and the info I have given is of use.
    Col
  • In reply to Former Member:
    Colin Welsh said:
    Daniyar,
    Yes, I have. Initially, when installing the DeltaV OPC Remote on VM, it has all needed DCOM configuration set autonatically. I`ve check it manually according to DeltaV Online Books Manual.
    The DV Server as well AS OPC Client are on same subnet.
    Daniyar Mamenov
    Projects - ME&CIS