Hello,
I have a flow PID loop that is AUTO normal with setpoint of 400 pph.
I have a CALC block setup that when another valve open the setpoint changes to 15,000pph.
How do setup the PID to gradually increase the setpoint from 400 to 15000 pph without making a big one step change? How do I use SP_RATE_UP parameter?
Thanks for the help.
In reply to SBPosey:
Thank you SBPosey for replying
Please confirm my calculations. My PV_Scale is 400-25,000 pph and the set point can be anywhere in that range. I would like 5 minutes for working SP to go from 400 to 25,000 pph, the same for downward set point change.
SP_RATE_UP = 82
SP_RATE_DN = 82
So does this mean if my set point is 400 pph and the setpoint changes to 18000 pph, the set point will go up by 82 every second? So 482, 564, 646,......, until reach 18000?
Thank you