good morning, i have a signal 0-100%, I need limite this signal to a fall of 10% per second, the rise did not confine me anything,
Regards.
For an input you can use the RTLM (Rate Limit) and configure INCREASE_MAX (100), DECREASE_MAX (-10), ENABLE (1), TIME_UNITS (Secs). Wire the input signal to IN and the OUT will be the raw value on increase or the limited value on decrease.
If the signal is an output, you can use the same block or you can configure on the AO block SP_RATE_DN to 10 and leave SP_RATE_UP to 0.
Regards,
Matt
In reply to Matt Stoner:
thanks
In reply to Irving_Aguilar:
The INCREASE_MAX and DECREASE_MAX are in terms of engineering units per time units, so if the requirement is 10% per second and the input signal is not a 0-100% signal, then you will have to ensure the signal is either scaled from 0-100% or configure the _MAX parameters based on the scale you need.
In reply to bhushan619:
The rate limit block, RTLM, has an output "ROC" that is the current rate of change. You many need to expose this parameter as an output of the block. Note that this ROC is a "scan to scan" rate of change and can be affected by noise on the signal. Books on-line says this about ROC "The filtered rate of change of the IN parameter. ROC is an indication that is independent of the scan-to-scan rate of change used by the block algorithm to determine OUT."
I often create my on "rate of change calculator" to be less affected by noise on the signal. I do this by wiring the signal to both the plus input of a subtract block and to a deadtime block. The output of the deadtime block is wired to the negative input of the subctract block. The output of the Subtract block can be divided by the deadtime setting to get the ROC. The ROC is an average ROC over the deatime. I gernerally use 10 -20 seconds. If you execute the module and function blocks at one second, the ROC will update every second even though the ROC is averaged over the deadtime which is longer.