Risk with Downloading Changed Setup Data

Hello,

I added a name state to a name set. Now I have blue triangles next to all my controllers.

If I download changed setup data for each controller will this effect operations or bump the I/O just like downloading the controller? Are there any risks?

Thanks

2 Replies

  • nevermind this question.

    There is no risk with downloading the setup data to operations.

  • I download changed setup data to all my controllers whilst online and have never experienced any issues after changing name sets

    Sent from my iPhone

    On 24 Jul 2014, at 21:25, "darrell" <bounce-darrell@community.emerson.com> wrote:

    Hello,

    I added a name state to a name set. Now I have blue triangles next to all my controllers.

    If I download changed setup data for each controller will this effect operations or bump the I/O just like downloading the controller? Are there any risks?

    Thanks