Hi, This is Regarding Switch over in Redundant AI Cards
During diagnostics, It was observed "?" in Redundant AI Card.
The summary of Diagnostics:
Switch_Aail = Switchover Avaliable ( Avalibale - common faults, Resolve Problem and Clear Saved Fault Information)
POINTEG = BAD
PStatus = Need to clear error to be able to switch.
Note: There are no other errors and all channels are Good.
The two Redundant cards getting i/ps from the common i/p terminal block.
---------------------------------------------------------------------------------
Questions are :
1. Where the fault information will be stored anywhere ? to Know the Reason.
2. I suspect - Fault occurred due to a channel i/p loop is open for maintenance & lt is closed after work. If so, in this case - if any other channel of that card is open (or) Card itself fails - whether Switch over will happen to Redundant card, without clearing the fault information?
3. Pl, Mention in which cases switch over will happen with different possibilities.
-----------------------------
Thanks in advance.