Selecting a Named Set from the Drop Down Menu

Hello all,

I'm currently trying to configure a control module class and I created a few new named sets to use for my DC1 block. However, when I try to select the named set I want to use from the drop down menu, I'm only presented with 5 or so named sets and it will not let me browse for any more. I can type in the named set and it will allow me to input the named set that way without an issue.

What am I missing here that it won't allow me to select any more named sets?

  • Most likely you are missing a value in the named set you are trying to use.

    For the FV_D/SP_D/PV_D named set you need to have 0, 1, 2 and 255 values.

    For the State named set you need to have 0 - 11 and 255 values.

    For the Fail named set you need to have 0 - 8 and 255 values

    There can different conifgurations of User Selectable and/or Visible but you have to have the same number of values with the named set.

    Review the default named sets for a Forward/Reverse motor (mtrfr, states_mtrfr and fail_mtrfr) to see what the values should be as example for three states.

    Regards,

    Matt

  • In reply to Matt Stoner:

    Thanks Matt,

    That was my first inclination but that's not the case. I'm specifically trying to select a Fail named set that I created but all that shows up as selectable are the default fail named sets.

  • In reply to deltafiveengineer:

    You must have the named set in a named set folder and not at the root level of named sets, if you move it to the root level it should show up.

    An unfortunate "feature".

    Regards,

    Matt

  • In reply to Matt Stoner:

    Yep, thats exactly it. For some reason I thought I could browse to it but it does seem ridiculous that I can manually input it but not select it.

    Thanks for throwing me back on path Matt.

    Much appreciated!