Hello all,
I'm currently trying to configure a control module class and I created a few new named sets to use for my DC1 block. However, when I try to select the named set I want to use from the drop down menu, I'm only presented with 5 or so named sets and it will not let me browse for any more. I can type in the named set and it will allow me to input the named set that way without an issue.
What am I missing here that it won't allow me to select any more named sets?
Most likely you are missing a value in the named set you are trying to use.
For the FV_D/SP_D/PV_D named set you need to have 0, 1, 2 and 255 values.
For the State named set you need to have 0 - 11 and 255 values.
For the Fail named set you need to have 0 - 8 and 255 values
There can different conifgurations of User Selectable and/or Visible but you have to have the same number of values with the named set.
Review the default named sets for a Forward/Reverse motor (mtrfr, states_mtrfr and fail_mtrfr) to see what the values should be as example for three states.
Regards,
Matt
In reply to deltafiveengineer:
You must have the named set in a named set folder and not at the root level of named sets, if you move it to the root level it should show up.
An unfortunate "feature".