Hi colleagues,
We have a number of the DIN-mounted smart switches VE6041 in our DeltaV system. Specifically, their model number is VE6041F05C1. Since installation, we have received a number of hardware/device alarms associated with these switches, and from looking at their on-line control module, we see that the temp of the switches had exceeded the 50 degrees C (122 degrees F) setpoint. The general internal cabinet's temperature (where the switches are located) is about 85 degrees F typically. Occasionally, when the general temperature of the cabinet rises to about 95 degrees F, the high temp alarm situation of the switches occurs. So what we have seen is that the temperature of the switch is consistently about 30 degrees F higher than the general internal temperature of the cabinets. In other words, if we want to bring the temperature of the switches down, the obvious way is to bring the general temperature of the cabinet down which is not simple for us at this point.
I have some questions:
1. Has anyone encountered this situation? I so, what measures did you take to alleviate it?
2. Is there a KBA or similar information about the high temperature of the switches from Emerson? Is there a known issue with these switches? Is there a recommended way to install these switches?
3. Our goal is to make sure we don't shorten their lives with constantly running hot. We are looking at some internally mounted spot blower to provide more airflow over these switches. What recommendation can you give us?
Thanks
3.
Andre Dicaire
In reply to Andre Dicaire:
Thank you for your response, Andre.
For all of our cabinets, we have seen a consistent delta of about 30 degrees F between the switches temp and the ambient temp (the ambient temp sensor is in the general area of the cabinet about 15 inches away from the area of the switches). We suspect this is an airflow issue as you mentioned about obstructions. As you can see in the picture, our switches are surrounded by Panduit (similar installation for all our cabinets).
I want to confirm first that there are no known issues concerning the high temperature detected by the switches (its electronics, manufacturer components, over sensitivity of sensor, etc.) before finding a resolution of increasing the airflow around the switch (which will be a challenge as you can see from the picture).
I absolutely agree with you about the product temperature that is crucial for reliability. That's why at this point I must trust that this high temp we see is in fact accurate and find a solution.
In reply to ha nguyen:
Thank you again for your input. Thanks for taking the time to write. It's quite comforting I must say.
The max ambient temp rating for the switch model we have is 60 degrees C (140 degrees F) per Emerson literature and it does state this is "Ambient Conditions". Our average ambient temp in our cabinets is comfortably below the max from what we have seen so far. It does seem counter-intuitive to have the default setpoint be without some expected offset, but then again I expect offset amounts will vary for different cabinets designs.
Best regards.
Just want to add this KBA (for those that may be interested) that I just received from our local Emerson partner. It's supportive to the input from Andre. Thanks again.