Dear All,
During an upgrade indeed the controler looses its downloaded configuration. For this reason the process has to be brought to a safe, stable state. This might be a shutdown depending on your plant. In case you have redundant controllers, you have the possibility to upgrade one controller at a time. Then after a switch the second controller can be upgraded. Here, the plant can be operated during the upgrade process, however, it still would be wise to bring the proces to a stable status.