DCS alarm F0006322 error 91 communication alarm

I have no idea what this alarm is? it appeared a week or so ago, I have looked everywhere for it? any help would be appreciated.

6 Replies

  • Tom, Do you currently or have you ever had a fieldbus device with this tag number configured in this database?  

    Regards,
    Mel

  • In reply to Mel Travis Layton CAP:

    Not that I can ever recall Mel, but I am double checking
  • In reply to Tom Light:

    No I have been here since construction. we have nothing in that range
  • Could you send a screen capture of the alarm?  Is it associated with a particular alarm area?  
    Thanks,
    Mel

  • In reply to Mel Travis Layton CAP:

    here is a screen shot Mel it was on 04/14/2020 3:22:01

    thanks for taking a look it doesn't appear to be associated with any area.

  • Hi Tom,
    The screenshot might be the clue needed.  It looks like you might be communicating with a PLC via Modbus or VIM, etc.  Can you check to see if this alarm could be driven from one of your ports or datasets?
    Mel