Termination board for SIS Logic Solver

Dear Expert

Please help me to know about recommended  termination board in Marshaling cabinet for  SISTm Logic Solver

Thanks in advance

  • In reply to Jason.Brumfield:

    the SLS1508 does not have isolated IO. all its IO signals are powered and grounded by the SLS1508.

    The CSLS has a choice of CHARMs

    you can review the Product Data sheets to see wiring connections.

    They do not have recommended termination boards. the SLS1508 terminal block is mounted directly on the SLS carrier
    you would wire these terminals to a Marshalling terminal block strip where you can add interposing relays and other wiring features.

    The CSLS is designed for direct wiring of field IO signals to the CHARM terminal blocks. the CHARM provides signal disconnect and circuit protection. Fusing is provided in some cases. you do not need marshalling terminals with the CSLS.

    Andre Dicaire

  • In reply to Andre Dicaire:

    Many thanks for your Response