Hi Everyone,
We are facing some issue with Samson 3731-5 FF positioner. According to Samson  their AO function block changed to OOS mode even they put to Normal mode/ restarting the positioner. They are asking whether DV is writing to change the OOS mode.
Can DV FF function block cause this issue? Require some solid proof to say that it is not DV issue. Could anyone advise please?
Thank you.
  • A few suggestions . . . .
    1.) Check the "Event journal" (using PHV) to see if any pertinent events are recorded. Make sure the proper areas are being monitored to catch such events. A block mode change might show up there.
    2.) In "Control Studio" or DeltaV Explorer, check "Module references" to see what blocks or other modules might be writing to the "mode".
    3.) I've seen the mode of other function blocks default to OOS when there was a configuration error (configuration of the device).
    4.) Is the "CAS_IN" of the AO coming from a DeltaV PID block or another device's PID block, or some other block?
    5.) Is BKCAL_OUT connected to the upstream PID block's BKCAL_IN? Is "OUT" of the AO block connected to anything?
    6.) Is this the only instance where a Samson valve is having problems? If they work elsewhere what is different in this module?
    Perhaps you can post a screen capture of the module.
    I have not seen any instances where DeltaV changes the mode of blocks - without specific coding to do so.
  • In reply to John Rezabek:
    Dear John,
    Thank you for your suggestions:
    I do have screenshot from our service engineer from site which was done as investigation analysis for customer to Response to Vendor as follows:
     2440FV-112 failure.
     •            What’s happen after 300s if a communication lost to the positioner?
        The valve will close by follow for FSTATE_VAL =0% as setting of AO block.
    From the point of review, we did not find any signals from the H1 Card fieldbus by Hardware error/Communication failure . These segments consisted of these tags.
    Segment design :
    When we went to the Filters Alarm of each module in the segment on Delta V DCS , there was only Tag 2440FV-112 with alarm the communication failure at 10:50:24 AM on 8 Dec, 17 as shown below picture, where the other device is still normal (Good Service).
      Actual activities for system/device diagnostic
    - No hardware H1 Card of  fieldbus failure.
    - No Accident removed of Terminals
    - No Loss of input signal to the valve (ie AI function block)
    - No Loss data by segment  macrocycle calculation out of limited (Requested Time : 250ms and Actual Time : 165ms) is good
      • 2440FV-112 alarm module (Positioner Device)
    Then we open Block error properties for AO block show : Out of Service (OOS) only 1 selected value for AO positioner.
    According to Samson investigation report number , They have block error by the Out of service also.
    1.VIEW4_3731_5_2123860_2017-Dec-08 2440-FV-112 (PTTGC5) out of servic ...
    Section 7.1.2. Block errors  ,7.1.2.2. Positioner (AO, TRD) and 7.1.2.3 Process controller (PID) with we assigned to control in the field (PID and AO block located in valve positioner)
    7.1.2. Block errors
    Normally, FSTATE_TIME and FSTATE_VAL are setting for AO Block  of all control valve module in ARO 2 plant .But we never saw AO block mode executed  to Out of Service.
    •            Switch the positioner to operating mode LO (as you can see on the next screen shoot) and is the valve position 0%?
        I didn't know what is the matter but I understood If the device is locally set to the MAN mode, the AO Transducer Block is set to LO. DCS never change/write mode during on normal operation. (No permissive work by senior operator / Shift supervisor and Shift manager approval) It might happen after who go the diagnostic test to check for common error or not because of the incident on that day, we just only  have a Commissioning / Decommissioning to change the new valve positioner on DCS Delta V exploring with download after they have requested to replace the new device ( positioner) from Field Maintenance team in the afternoon of that day.
      • Static Revision Counter
    Static Revision Counter ( Counters from 14 --->16)
    : This is possible when they changed the parameter in the resource block during a device change. (Use spare from 2100FV-1) The difference parameter setting See Audit trail show the event type by configuration change during positioner replacement .
       Did you observe for Classification report error?
    From the picture below, you will see the message ( ie Maintenance required, Device need Maintenance soon.)
      What is a recommendation?  Do we need to reset / restart the processor of positioner ?
    Should you have any suggestions on this matter ,please advise
  • In reply to NeverSayGiveUp:
    You can try a reset - which of course will affect the process if it is running.
    Also ensure that the TRANSDUCER block of the positioner has permitted modes AUTO, MAN, OOS and you may have to manually switch the mode of the transducer block to AUTO. I only have one Samson valve / positioner and it is a few years old. Model 373X-5 revision 1. If I use the DeltaV "EDDL" display (versus the DTM) there is a selection under "configure/setup" for "Advanced Positioner Valve View". I see about 20 tabs but one of them is "Operating Mode". Look here and see if "Target Mode" is Automatic and "Actual Mode" is tracking (shows the same mode as "Target"). (assuming the version you have is similar).
    If "Target Mode" is not Automatic, set it to "Automatic". This mode is separate from the AO block mode, but it must be in "AUTO" for the AO block to function.
    If "Actual Mode" appears to be stuck in OOS (won't go to AUTO) - this usually means there's some configuration problem. Maybe a calibration of the positioner will clear it. Feedback mechanism might be misaligned or broken. Air pressure too low.
    I also see settings here (in the transducer block settings) for fail behavior "Set to FailSafePosition" which you may want to disable if you are also using the FSTATE_TIME and FSTATE_VAL in the AO block.
    Everything looks good in the schedule. Everything is commissioned and downloaded, right? No blue triangles on any devices or the port?
    If you have another positioner, I would try to wire it up and download, and see if the behavior is the same.
  • Would it be possible to provide your email address and we will have our local office to contact you.
    Hi John,
    When you are saying to check TRANSDUCER block of the positioner has permitted modes AUTO, MAN, OOS and you may have to manually switch the mode of the transducer block to AUTO.
    You are referring to ask the valve vendor to check in their valve itself right?
    When I right click the Transducer block in DeltaV there is only properties option which has nothing as above.
    We can check and change these from AMS device Manager, right?
    I would drill down to the segment (port) in DeltaV Explorer, right-click icon for the Samson valve, and select "Configure/Setup". The "EDDL" driven dialog box should appear, with possibly several transducer blocks - in our application there appear to be transducer blocks for discrete applications. You want to select the one for the "Advanced Positioner Valve View".