Hi All
we have a problem in our Delta V system of M5 series, after a power cutoff on UPS system all I/O cared error led start blinking and the cards are not visible at Delta v explorer with question mark indicator we tried the following to solve the problem and unfortunately it's still exist
1- download the program and I/O configuration
2- auto sense for I/O cards
3- power reset for the controller
4- power supply circuit was checked and it's healthy for all cards
after figuring the problem in DeltaV diagnostics all the cards show Bad , and communication problems as in the attached photo , please help me I only have two weeks experience with DeltaV system
Hello Mohammad,
I have ran into this issues twice over the years. Due to the power surge, it damaged the 2-wide railbus communication to the 8-wide. Try replacing your 2-wide