Dear all,
I shutdown my server in the DeltaV database administration today for some reason.Now when i tried to reconnect to the server it gave me an error that it can't connect with the deltav server on the Engineering Work Station. In the services , the deltav services were started . Now to remedy the problem i restarted my server machine but the deltav could not start the start up services. Later on when i plugged out all the network out of the switches and turned on the server , the services started and it ran fine but i can't do it all the time.The system is currently in an engineering facility and later on it will be shipped to the site. I need a solution to this issue that is permanent , and i don't want to plug in and out my whole network , everytime this issue comes up.
Thanks and Regards
ASIM
Hi,
If you have access, look at CTS NA-0800-0067. I faced a similar issue and this solved it.
Basically it can happen that an OPC client is connecting to the DeltaV OPC server while the machine is starting up. If the OPC service starts up before the DeltaV service, the DeltaV service will not start.
Istvan
In reply to István Orbán:
Dear Experts,
we are facing a database connection problem.
Our Plant: 3 Engineering Station, 13 Operator Station, Hist Server 1 and 2 , BackUp Server.
Since a few days, when we want to open DeltaV Explorer, this message Pops up: "Connected with the database server but failed to open a database connection...........Reasons:Access is denied".
This message appear on both used Engineering Station randomly. One time this message appears maybe one hour later Explorer opens normally.
A few days before this symptoms appears, my colleague ran a "DeltaV Wokstation Configuration" (with DV workstation File, exported on PROP+) on one of our Engineering station.
Anybody knows something about this problen
Thank you for your help