I know running 16x9 is not supported by Emerson with Version 11.3.1 but has anyone done this? We are trying to purchase a large (60") screen to run a L1 Overview Display. The issue with buying a 60" 16:10 is they are pricy and it appears Emerson is now supporting 16x9 in version 13.3. I would like to buy a large 16x9 at a fraction of the price.
Thanks,
Mike
In reply to John Rezabek:
In reply to mdevienzio:
You may be able to tell computer to run the monitor to run at 1680x1050 in which case it would just stretch the image to fill the monitor, otherwise above is what a single monitor DeltaV Station looks like at 1920x1080
You control the picture with the "Layout" file. The example uploaded by Mike utilizes the default DeltaV layout which attempts to preserve the 4:3 aspect ratio and throws in the picture history/ faceplate history / alarm summary which we did not find particularly useful.
Also in Operate "user preferences" select the "Disable Auto Scale Feature" in the "Picture Preferences" tab (check the checkbox).
Our layout file utilizes the entire 1680 pixel width for main picture. You can see old Duncan is stretched a little. The template for 1680 x 1050 is found under "templates" in your PIC directory.
Incidentally we are also using a large screen for an overview display, albeit in 13.3.1. It would have worked in 11.3.1 also.
Note that the toolbar and alarm banner (old one in our case) can also be sized for the wide screen . . .