Hello,
I have a question about steam tables. What im trying to do, is look up the pressure of steam at a given steam temperature. I see they have a 'TSS' function block in the function block libraries, but from the looks of it, it calculates the steam temperature at a given steam pressure, and not the other way round. Unless I am mistaken or am overlooking something. I know I can calculate this, but have been told and advised to use the 'built-in' functionality that DeltaV already provides.
Any help would be greatly appreciated :)
Thanks!
I guess you are looking for SST function block see below
Saturated Steam Properties - Given Temperature (SST) function block
The SST function block calculates the steam enthalpy, entropy, specific volume, and pressure for saturation conditions specified by a given temperature.
The block calculations apply to saturated steam. The calculation is limited to a temperature range of 32°F to 705.103°F (0 to 373.946°C).
In reply to FAKHAR AHMAD P.Eng.: