I hate to see knowledge exchange left in the obscurity of an email inbox. Here's a recent exchange I wanted to share in case it helps someone with similar questions.
Question:
I am having some trouble with the Cascaded Master controller tuning in the DeltaV. The masters are usually looking at level or pressure and cascaded to flows. I usually use low to moderate Proportional (2 to 12) , very little if any Integral( >400) and then Derivative anywhere between 5 and 50. I notice that that even though the error is small in the master controller, often the output will change will change rapidly up or down. I can sometimes see in my historian that there may have been a small noise or bump in the master Controller process variable. I am wondering if the standard control algorithm where P& I work on the error and Derivative looks at the PV may be causing this? I am going to change equations in the Master to the P,I & D work on the error collectively, to see if I get a more buffed response from the algorithm. From what I have described, do you have any thoughts?
I shared this question with Emerson's James Beall, whom I've featured many times on the Emerson Process Experts blog. Here's a link to one of his Emerson Exchange presentations, Interesting and Useful Features of the DeltaV PID Controller.
James responded:
I’ll be glad to visit with you regarding your questions on Cascade control in DeltaV. Here are some comments on the topic in preparation for a discussion if needed.