Hello,
I have a valve setup in the field on Analog Output Hart Card.
I am getting intermittently ( approx every 15 minutes Not Communicating With Device) warning alarms, but the valve is still working (off the 4-20mA signal) and controlling.
1. From the HART Statistics screenshot, what does Timeout Errors mean?
2. Does the Not Communicating with Device warning mean I am losing the HART communication with the Device?
This is the 2nd AO card I placed the valve on and the same issue. The previous AO card was giving me I/O failure and the 4-20mA was loss so the valve will go to fail state. This also was intermittently. To get valve working again, we reset the power to valve.
Also, I am unable to connect to device with AMS
Any ideas what could be causing this issue? Thank you
In reply to Kris Chandrashekar:
In reply to DCS Newbie:
Kris Chandrashekar said: By the way, your case is not an exception. Over a period of time, many users run into the same issues and will just work with HART disabled channels.
Could this because of noise or electromganetic interference around the valve in the field? Maybe certain HART devices are senstive the noise.
Thank you
Kris Chandrashekar said:(Since the AO wiring is disconnected the 24 Volts DC is no longer available to the control valve).
Thank you.
Help me understand. So the DeltaV AO card is providing a 24V DC and 4-20mA to the control valve for power and control?