fieldbus communication

Hello;
even if the flow meter is commissioned but I can not downloaded it gives me the following message even when I make a change in the configuration from AMS I see at the transmitter.
thank you for your help.

Best regards.

Butler faith.

1 Reply

  • There is not just one cause of this issue.

    There are 2 major things to check first in the device’s AMS screens:
    1. Make sure Resource Block Permitted Mode has both Auto and Out of Service checked.
    2. Make sure Resource Block parameter Write Lock is disabled.

    For a download, DeltaV must put the RB mode to OOS. If either of these conditions are not set correctly, it will prevent the change to mode: OOS.

    I hope this will help.