Continuous Historian Not Running/Won't Start

We have a small lab scale DeltaV install (one ProPlus and one Controller), and we had to rename the ProPlus due to IT rules (I know, its not good to rename one, but to get full access we had to).  After goign through the reconfiguration, everything is fine exept the Continuous Historian won't run.  Continuous Historian Admin tells us "The Continuous Historian Server is not avaliable.  Please start the Continuous Historian Server and try again."  None of the history data is at all important.  I'd just like to remove/re-install the historian if that would get it working.  Is there a written prodeduce I can follow for that?

6 Replies

  • From BOL on how to re-register the CH database with the new workstation name:

    Open a DOS window and run the following command to register the new database:
    C:\ooinstallfd -nocheck -standalone -lockserverhost COMPUTERNAME X:\DeltaVHistory\DvCHdb.hdb

    (where COMPUTERNAME is the new name of the Continuous Historian workstation and X:\ is the drive where the DeltaVHistory folder exists). Then reboot the machine.
  • In reply to Steven Estes:

    Before performing that command however I believe you will need to rename the CH directory (D:\DeltaVHistory) to something else and paste the C:\DeltaV\fdbhist directory in as the new CH directory (D:\DeltaVHistory). You may need to stop the DeltaV services first to do this. Once youve recreated the CH directory doing this then you can run the command above and reboot the machine.
  • In reply to Steven Estes:

    Thank you very much! The second step was needed before it worked. One other detial incase some else has the same problem an sees this thread, in our system ooinstallfd is not in the root C:\ directory. It is in a named path though, so the c:\ is not needed at all. (It maybe should have shown C:\> )

    The command we used was then:
    Open a DOS window and run the following command to register the new database:
    ooinstallfd -nocheck -standalone -lockserverhost COMPUTERNAME X:\DeltaVHistory\DvCHdb.hdb

    (where COMPUTERNAME is the new name of the Continuous Historian workstation and X:\ is the drive where the DeltaVHistory folder exists).
  • In reply to brenton.fox:

    Great work documenting the solution, gents. Thanks, !

    Best Regards,

    Rachelle McWright: Business Development Manager, Dynamic Simulation: U.S. Gulf Coast

  • I'm very glad you were able to get the Historian running again. I haven't tried to rename a ProPlus in a number of years, but remember it being a very, very bad idea on version 7 (terrible idea on v6.3).

    I realize this is a small lab scale DeltaV, but I hope there is either a clear line of separation between IT responsibility and Non IT responsibility for any real production systems you have. Either that or hopefully anyone pushing IT rules down to a process control network fully understands the priorities and needs compared to typical IT installs. They are not the same. This concept has worked well in the companies I've been with. Draw a clear line of responsibility, but work together.
  • In reply to Michael Moody:

    Good insight, .