Hello,
need advice how to connect Profibus-PA instrument to Profibus card on DeltaV.
should i add something in between? i found DART Power Hub – SK3 from http://www.pepperl-fuchs.us/usa/en/classid_2756.htm
is that the correct device?
thank you,
A Profibus PA segment can not be directly connected to the DeltaV Profibus dP IO card. You will need a Profibus dP to Profibus PA segment coupler to connect the PA segment to a DeltaV Profibus card. There are several manufacture of these couplers including Siemens and Pepperl+Fuchs. http://www.pepperl-fuchs.us/usa/en/classid_428.htm It looks like the device you included in the link would work as well. Rob Sentz "RizalDL" ---09/20/2014 12:39:18 PM---Hello, need advice how to connect Profibus-PA instrument to Profibus card on DeltaV. should i add so
In reply to Robert Sentz:
We are using one from Pepperl+Fuchs, I think it is even in some Emerson recommendation. It works nicely, seamlessly, it's completely transparent as far as DeltaV is concerned (it does not have a Profibus address, etc.). BUT if your slave is using some special Profibus+PA features, you will probably not be able to use them from DeltaV. For example, our slave does not have jumpers or a menu to set its address, the master needs to give it with a special command. So we need to use a third party device to give it an address, after that the communication works fine with DeltaV too.
ASKPSS has answer with exact model, it is KT-MB-GTB-2PS from P&F
thank you all.
In reply to István Orbán:
hi Istvan, what third party devices you use for?
In reply to RizalDL:
This is the third-party tool we are using: www.procentec.com/profitrace2. We mainly use it to generate diagnostic reports on the quality of the bus, this address setting is just a minor thing.