Dear All,
I am facing the following problem with the PCSD faceplates
Using Delta V V11.3.1 and PCD lib version 11C.
Have master slave modules. From Master Module's faceplate I could see the Slave module name. if I click on it, itshould open the Slave module's Faceplate. But it is not opening the slave's one.
The same is happening with Slave module's faceplate as well. i.e from the Slave module's faceplate could not open the master module faceplate by clicking on the Master module's name.
Control Modules are configured properly and downloaded. Funtionality works good from Control Studio.
Kindly share the solution
Thanks,
Manik
In reply to AdrianOffield:
Length is small.. only 7 letters
CAS IN PATH with the Module name/OUT
Slave 1 is only module name
No Zones
faceplate is PCSD_Loop_52_FP
In reply to manik:
What is configured for the module faceplate for the module name in Slave 1?
Are you getting an error message when trying to open the faceplate(s) - if so what does it say?
In reply to Matt Stoner:
Matt,
Slave1 I have given the Slave's module name.
Is the name of slave/master control module correct?
Have add or remove any frsvariables in the specific PIC ?
Is it only happening with these two loops ? if it's not
Just Complie the VBA script for the PCSD_LOOP_52_FP and see if you are getting any errors , if there is pl high light & share it with a snap shot