Handshaking between PCSD HCD Faceplate
Dear All,
I am facing the following problem with the PCSD faceplates
Using Delta V  V11.3.1 and PCD lib version 11C.
Have master slave modules. From Master Module's faceplate I could see the Slave module name. if I click on it, itshould open the Slave module's Faceplate. But it is not opening the slave's one.
The same is happening with Slave module's faceplate as well. i.e from the Slave module's faceplate could not open the master module faceplate by clicking on the Master module's name.
Control Modules are configured properly and downloaded. Funtionality works good from Control Studio.
Kindly share the solution
Manik
  • What is the parameter path specified in the CAS_IN_PATH and SLAVE1 paramters?
    Sometimes if you specify a long path, the faceplate can’t resolve which faceplate to open.
    From: manik [mailto:bounce-manik@community.emerson.com]
    Sent: Friday, August 29, 2014 2:31 PM
    Subject: [EE365 DeltaV Track] Handshaking between PCSD HCD Faceplate
    Dear All,
    Manik
  • In reply to AdrianOffield:
    Length is small.. only 7 letters
  • Just text or with “/” characters?
    Which faceplate is the module configured with Loop_FP (default) or something else?
    Are you using Zones?
    Sent: Friday, August 29, 2014 3:18 PM
    Subject: RE: [EE365 DeltaV Track] Handshaking between PCSD HCD Faceplate
    CAS IN PATH with the Module name/OUT
    Slave 1 is only module name
    No Zones
    faceplate is PCSD_Loop_52_FP
  • In reply to manik:
    What is configured for the module faceplate for the module name in Slave 1?
  • Are you getting an error message when trying to open the faceplate(s) - if so what does it say?
  • In reply to Matt Stoner:
    Matt,
    Slave1 I have given the Slave's module name.
    Manik
  • Is the name of slave/master control module correct?
    Have add or remove any frsvariables in the specific PIC ?
    Is it only happening with these two loops ? if it's not
    Just Complie the VBA script for the PCSD_LOOP_52_FP and see if  you are  getting any errors , if there is pl high light & share it with a snap shot