HOW TO RESTRICT THE ACCESS TO THE IGNORE PV PCSD FACEPLATE

I need to restrict the Operator access to the IGNORE PV selection  and allow it only to supervisory level . How to restrict this access ?.

1 Reply

  • Under Setup > Security > Parameter Security in DeltaV Explorer will let you change the security on any parameter. By changing this was from "control" to "restricted control" or "tuning" (depending how you do your security on your system will probably accomplish what you want. Looking at the vintage of your PCSD that I can see, I believe that "IGN_PV", but you can get the exact version by looking in control studio at the DC_CTRL composite in front of the DC block as that's usually where the Ignore PV was handled.