Hi Guys,
I tried searching this site, BOL and the internet. no luck.
I would like to be able to have two instances of a faceplate open at the same time. I want to view the PID faceplate of two loops at the same time (each loop would provide data to 'its' instance of a PID faceplate. Is this possible/easy?? If so, how would I go about it?
Cheers,
Eric
1. Edit the script in usersettings.grf. You need to uncomment a line to enable multiple faceplates and to set the maximum number.
2. Run the update popup pictures utility in DeltaV Operate. This is a button that looks kind of like a faceplate and is located on the DeltaV Utilities toolbar.
Also when you have one faceplate opened, check the "pin button" to lock it
Niklas Flykt
Klinkmann Oy
Key Account Manager safety products
nikfly@gmail.com