Dear all,
I have a project having multiple effects (CEM Blocks) and their causes (VTR blocks) on the same screen.I want to pin multiple VTR or CEM faceplates at the same time but i can only pin one CEM and one VTR. Is there a way to pin multiple face plates of the same type on a single screen example multiple AI or DI screens?
Regards
Muhammad Asim Butt
You need to run the pop up picture replication script in operate configure. It is a tool bar button that looks like a white faceplate icon. It will create indexed copies of each fp/dt to allow multiple copies opened simultaneously. Search this forum; I recall someone did a pretty good write up about it.
In reply to Youssef.El-Bahtimy:
In addition to the tool bar button Youssef mentioned, you'll also need to find the following line in your user_settings.grf or WorkstationName_Settings.grf file and uncomment it (It's somewhere around line 567):
'frsVariables.GN_IA_LOCKENABLED.currentvalue = 1
Good Luck!
P.S. Don't do that for "Operator Keyboard Systems." Also, you'll also need to make that change on every workstation if you arent using the user_settings.grf