I have this script in a CALC block. I have two identical productions lines, with the same equipement name, except for the line number: 2211 and 2212.
Now, I have the operator select which line he's configuring.
Here's the sigle line example:
   '//2211-YV03/DC1/SP_D.CV' := 1;
   '//2211-YV04/DC1/SP_D.CV' := 1;
   '//2211-YV06/DC1/SP_D.CV' := 1;
I would like to modify it for something like that:
if LINE_SEL = 1 then
 LINE := "2211";
else
 LINE := "2212";
endif;
   '//LINE-YV03/DC1/SP_D.CV' := 1;
   '//LINE-YV04/DC1/SP_D.CV' := 1;
   '//LINE-YV06/DC1/SP_D.CV' := 1;
OF course, this doesn't work, as well as the two dozen other possibilities I've tried.
Any idea how to achieve this? Rather new to DeltaV, going to my training next week.
Pierre.
  • I ran into a similar problem a couple years back.  I wanted to display the string name of the person currently on call given a set of conditions.  My solution (probably one of many) was to store the strings in input parameters and reference the parameter names in my logig instead of the strings.  This also allowed me to make online changes without having to download (should 2 people switch weeks).
    Here's my code:
    if 'IN1.CV' = 0 then '^CURRENT_ON_CALL.CV' := '^ONCALL_0.CV'
        else if 'IN1.CV' = 1 then '^CURRENT_ON_CALL.CV' := '^ONCALL_1.CV'
             else if 'IN1.CV' = 2 then '^CURRENT_ON_CALL.CV' := '^ONCALL_2.CV'
             endif;
        endif;
    endif;
    James Suisse
  • Hi Pierre:
    DeltaV has only rudimentary string handling capability, so for that reason (and for ease of troubleshooting) I would do something like the following:
    IF LINE_SEL = 1 THEN
      ‘//2211-YV03/DC1/SP_D’ := 1;
      ‘//2211-YV04/DC1/SP_D’ := 1;
      ‘//2211-YV05/DC1/SP_D’ := 1;
      ‘^OP_MESSAGE’ := “Line 1 selected”;
    ELSE IF LINE_SEL = 2 THEN
      ‘//2212-YV03/DC1/SP_D’ := 1;
      ‘//2212-YV04/DC1/SP_D’ := 1;
      ‘//2212-YV05/DC1/SP_D’ := 1;
      ‘^OP_MESSAGE’ := “Line 2 selected”;
    ELSE
    ‘^OP_MESSAGE’ := “No valid line selection”;
    ENDIF;
    ENDIF;
    The parameter OP_MESSAGE is a module-level string parameter that will display on the graphic or faceplate.  The message will prompt the operator if he somehow enters an incorrect value.
    Steve Elves
    Steve Elves | Control Systems Tech.
    From: Pierre_Dion [mailto:bounce-Pierre_Dion@community.emerson.com]
    Sent: Wednesday, March 13, 2013 5:26 AM
    Subject: [EE365 DeltaV Track] using a string in a command line
    Hi folks.
    Quick question:
     LINE := "2211";
    else
     LINE := "2212";
    endif;
    Pierre.
  • Hi Steve.
    Thanks a million.
    What you’re suggesting was actually my first choice, but I was wondering if there was a way I wouldn’t have to retype all of it for each production line, as much as to save coding time as well as to save the number of lines having to go through for troubleshooting. The actual program, for one line, has 70 lines of code…
    But if that’s the only way to do it…
    The OP_MESSAGE thing? Love it! I will definitely use it, at more than one place.
    Best regards,
    Pierre.
    De : Steve Elves [mailto:bounce-Steve_Elves@community.emerson.com]
    Envoyé : 13 mars 2013 10:28
    À : DeltaV@community.emerson.com
    Objet : RE: [EE365 DeltaV Track] using a string in a command line
    Hi Pierre:
    ELSE
    ENDIF;
    ENDIF;
    Steve Elves
    Hi folks.
    Quick question:
     LINE := "2211";
    else
     LINE := "2212";
    endif;
    Pierre.
  • Hello James.
    Thanks for the suggestion.
    I’ll keep this little code for our upcoming tech change. Will be useful.
    I doubt that this will solve my problem, as I have to take the content of the variable inside the call for the equipment.
    Anyhoo, as stated in my question, I’m going for the DeltaV training course next week. I will probably have my answer, as if it’s feasible or not, there, as by the other answers I received, what I’m trying to do seems to be quite tricky.
    Best regards,
    Pierre.
    De : James Suisse [mailto:bounce-suissejr@community.emerson.com]
    Envoyé : 13 mars 2013 09:40
    Here's my code:
             endif;
        endif;
    endif;
  • I've often used strings in command lines - the key is to use dynamic references and a parameter to store the string. Then you build your reference using the string as a portion of the .$REF field.
        LINE := "2211";
    ELSE
        LINE := "2222";
    ENDIF;
    '^/D_YV03_SP.$REF' := "//" + LINE + "-YV03/DC1/SP_D.CV';
    '^/D_YV04_SP.$REF' := "//" + LINE + "-YV04/DC1/SP_D.CV';
    '^/D_YV06_SP.$REF' := "//" + LINE + "-YV06/DC1/SP_D.CV';
    '^/D_YV03_SP' := 1
    '^/D_YV04_SP' := 1
    '^/D_YV06_SP' := 1
    That should take care of it - it might take a couple block scans before the dynamic reference connects, but if your block is continuously writing it should resolve itself.
  • Hi Pierre
    Just for information because this way to proceed may be to heavy :
    To concatenate strings to provide a module path, you need to use Dynamic Reference.
    - Declare 3 input labels (ie named TARGET1 2 and 3) witch type will be "Dynamic Reference"
    - In your programm, prepare the modules path string like you do with the LINE parameter + add the rest of complete syntax (1)
    - Wait for the connection of the 3 TARGET dynamic reference to be operational (2)
    - Then, you can use the TARGET label the same way you use a module path attribute :
        '^/TARGET1.CV' := 1;
        '^/TARGET2.CV' := 1;
        '^/TARGET3.CV' := 1;
    I think I remember that you cannot manipulate more than 5 dynamic reference labels at a time (in the same expression).
    Regards, Jack
    (1) String manupilation in a CALC expression is a little bit amazing sometimes because the compiler often preform an implicit conversion to numeric value.
    Your parameter contents must ALWAYS begin with an alphabetic sign (A/a to Z/z, space)
    If the first char is a numeric char, it will return 0 instead of the string.
    If you have this kind of problem, declare a new input label typed String and use it instead of the internal parameter. The rule about the fist char remains valid!
    Example of code :
        If LINE_SEL = 1 then
         LINE := "//2211";
        Else
         LINE := "//2212";
        EndIf;
        Rem I hope the heading double / will be read as a string ...
        '^/TARGET1.$REF' := LINE + "-YV03/DC1/SP_D.CV";
        '^/TARGET2.$REF' := LINE + "-YV04/DC1/SP_D.CV";
        '^/TARGET3.$REF' := LINE + "-YV06/DC1/SP_D.CV";
    (2) Waiting for dynamic reference connection :
    That's a problem in a CALC expression because you have to wait the next module scan to test it.
    You have to test that the .CST value to become = 0 on each TARGET 1, 2 and 3.
    So, you have to imagine a way to hold an OUT1 to 1 and connect it to an IN1 of the same CALC to know if you have to prepare le .$REF string values (when IN1 is 0), or if you have to test the .CST attributes to know if the connections succeed before assigning a value.
  • Hi Pierre:
    You’re welcome!  I hope it works for you.
    I use “OP_MESSAGE” all throughout my coding, especially in SFCs, to keep the operator informed as to what is happening.  I also use the LOGEVENT (see Books OnLine) command to write to the Event Journal things like logic selections that are NOT caused by direct operator entry – this command writes a string to the journal, and puts a timestamp on it as well.  Can be invaluable for troubleshooting and debugging.
    Good luck with your course – I’m sure it will be invaluable.
    Steve Elves
    Sent: Wednesday, March 13, 2013 7:53 AM
    Subject: RE: [EE365 DeltaV Track] using a string in a command line
    Hi Steve.
    Thanks a million.
    Best regards,
    Pierre.
    Hi Pierre:
    ELSE
    ENDIF;
    ENDIF;
    Steve Elves
    Hi folks.
    Quick question:
     LINE := "2211";
    else
     LINE := "2212";
    endif;
    Pierre.
  • In reply to Steve Elves:
    Thanks to all.
    The way to go seems to be with the dynamic reference. However, whatever I do, either with LINE := "2211" or "//2211"  or even "A//221" ( to put a real alpha character in front), the result  for the LINE variable is always 0 in the concatenated string. (endup with: '//0-YV03/DC1/SP_D.CV' in my dynamic reference.)
    Any idea of what I'm doing wrong?
    Pierre
  • I think you will find dynamic referencing to be very confusing and hard to troubleshoot.
    My advice to you is to go ahead and write the code out longhand.
    Steve Elves
    Sent: Wednesday, March 13, 2013 11:07 AM
    Thanks to all.
    Pierre
  • In reply to Pierre_Dion:
    Replace your internal LINE variable with a module-level variable that is explicitly defined as a string. That should force the interpreter to handle it as such. What does your binding expression look like?
  • Looks like a typo in the concatenation string.
    When a new variable is introduced (e.g. by typing error), this is assumed to
    be a numeric, and is assigned the value of 0.
    -----Oorspronkelijk bericht-----
    Van: Pierre_Dion [mailto:bounce-Pierre_Dion@community.emerson.com]
    Verzonden: woensdag 13 maart 2013 19:07
    Aan: DeltaV@community.emerson.com
    Onderwerp: RE: [EE365 DeltaV Track] using a string in a command line
    Thanks to all.
    reference.)
    Pierre
  • In reply to Maarten van der Waal:
    Yes.
    Maarteen confirms what I suggest : Using a String label instead of this internal string parameter and it works (just test it)
     You might also want to look at creating an SFC or State Driven module instead of burying all of this in a calc block with dynamic referencing.Either case will be much easier to troubleshoot in the future.  (Especially if you need to do this for 70 pieces of equipment for each line.)
  • In reply to Tyler Anderson:
    I'm going with Tyler's suggestion. I'm getting way over my head here with a lots of dynamic references, strings parameters, and the likes. I'm gonna endup with a calc bloc surrounded by input pararameters...
    Thanks a million for all your help guys. Really appreciated. I'll try the SFC.
    Piere.
    Pierre,
    I totally agree with Tyler.  The CALC block is a powerful block, but as you've found out, it can get you into a complicated problem, and difficult to troubleshoot.  Use the right tool. I often see "solutions" implemented in the controller that have nothing to do with the process control functions. Text manipulation is not what the controller was built for, so the text management is rudimentary.  I avoid string manipulation in the controller where possible. CALC blocks should be focused on executing an algorithm that can't be done with native function blocks, such as an iterative convergence calculation, complex equation, or a conditional expression that makes sense as an IF-THEN-ELSE.  Just because you can put it all in a CALC block, doesn't mean you should.
    In some cases, a CALC block solution could be more CPU load than a group of FB's, but even more important the CPU efficiency is visibility of the code for troubleshooting.  The SFC structure has powerful delay and confirmation statements, timers and execution flow that make the logic easier to work with.  That is often woth a view CPU cycles.
    Anyway, I was glad to see Tyler bring some sanity to the discussion :-)