Can Calibrate lock in iFix
Guys,
I would like to create a visibility condition for an object in iFix, similar to the one which is looking for the user key "CAN CONFIGURE".
DeltaV Explorer is animated in function of this
DVSYS.THISUSER\CAN_CONFIGURE.F_CV
(Somebody who has no config user locks, won't be able to open DV Explorer).
What I would like is to set a similar condition with the Can Calibrate user lock.
DeltaV iFix help states that there is an expression:
DVSYS.THISUSER\USER_CAN[AREA_NAME][LOCK_NAME].F_CV
I've tried to use
DVSYS.THISUSER\USER_CAN[REPLACE_DEVICE].F_CV
and
DVSYS.THISUSER\USER_CAN[CHANGE_DEVICE_DB].F_CV
which are Can Calibrate locks, but it didn't work.
Did somebody use this before?
Many thanks!
  • Barka -
    I've used this before for toolbar button visibility with the following syntax:
    DVSYS.THISUSER/USER_CAN.B_CV[AREA_NAME][LOCK_NAME]
    The Lock Name should be one of the locks listed in User Manager, so the lock name you would use is [CAN CALIBRATE], unless you have specific locks named "Replace_Device" or "Change_Device_DB" which I do not have.
    There is a KBA out there regarding the specific syntax.  Hope this is helpful.
    Kathy
    Kathy Pate
    Toray Carbon Fibers America
    Decatur, AL 35601
    kathy.pate@toraycma.com
  • There are three things that you need to tweak in your visibility condition:
    1) The slash after THISUSER needs to be a forward slash (/) instead of a backslash (\)
    2) Use .B_CV immediately after USER_CAN instead of .F_CV at the end
    3) Include the Area Name in addition to your lock name.
    DVSYS.THISUSER/USER_CAN.B_CV[AREA_A][REPLACE_DEVICE]
    The KB article that Kathy mentioned in her response is AP-0800-0121 (published 18 Sep 2008)
    From:        "barka" <bounce-barka@community.emerson.com>
    To:        <DeltaV@community.emerson.com>
    Date:        02/14/2013 08:21 AM
    Subject:        [EE365 DeltaV Track] Can Calibrate lock in iFix
    Guys,
    I've tried to use
    and
    Many thanks!