I see that the alarm lists can be set up to be filtered by Unit Module. Is it possible to filter the alarm banner based on Unit Modules as well?
In reply to KeithStThomas:
In reply to Kent:
Andre Dicaire
Ah, I see. Alarming is handled by Area. So, in this case you will have to create new Areas, one per Operator, add this new area to the Operator user in User Manager, and move the unit(s) to the correct Area. Then assign the Area to that Operator's workstation. The Operator will only be able to operate and get Alarms for Modules in the Area assigned to their workstation. Be aware attempting this while the process is running since moving modules from one area to another may result in loss of operator control. Ensure the new area is assigned to the operator and workstation first. I would even build a test module to confirm the operator has control and the alarms work before moving the units into the new area.
Any new Area will also have to be added to the Historian and Event Chronicle.