DeltaV Live: Slider

Hello, 

I’ve noticed an unusual issue with a slider component as I operate the functionality in DeltaV Live. The values and the cursor aren’t aligned as I operate high (95) and low (4) values.

It is only aligned when a median value is configured as highlighted at value 46.

Any help would be useful, thank you!

Abhishek

1 Reply

  • That is a known issue. I reported this a couple years ago. When you change the size of the slider. It create an offset in the position of the slide at run time. Suggest you log this with the GSC and confirm the incident is either still open or resolved on a late hotfix or possible v15.

    I can only say that there is no workaround provided and to not alter the slider size.

    Andre Dicaire