Hi All,
My question is regarding the DC-Device Control function block for motor control (3-wire VFD with non DeltaV integrated start / stop controls), I understand the DC operation but I am trying to figure out a special case where our operators who are not using a DeltaV workstation will turn on the motor in the field using start/stop push buttons. We do have feedback on if motor is running or not and that signal is put into the DeltaV as DC1 -> IN_1 (motor starter N.O. contact closure) .
What happens is from the faceplate (FP) side it shows a DeltaV motor status of “Stop” from DC1->SP_D (motor is actually running) and just below that the next box shows “Running” from the DC1->FV_D (Field devices) & OUT_D = 0.
Is there a way to momentarily pulse the FP start button in software when the IN_1=1 so as to update the DC1 module which then would put DC1->SP_D into "Running" mode and then allow the DeltaV operator to then stop the motor from DeltaV? Or should I have used a different DC motor function block or template?
In reply to ShaneG: