We are using 8851 in redundant mode and have analog module 8101-HI-TX (two nos in rack1 and another two in Rack2)...Total 4 racks.After some time, suddenly all the analog input module goes in failsafe mode..., the error seen in module diagnostic (workbench 8.4 sim8), shows "railbus comms mode" : short, under the "module diagnostic Data - Device status registers".Also other status seen are : -> module state : BIM in failsafe mode-> Last comms error : CNACKAfter recycling power to the IO base plate , the module is OK /or by using reset command from the workbench....But this problem reappears after few minutes again.Could you please help what could be the issue!regardsVikram