Please note We have a working DeltaV configuration that is in great shape and running awesome on the Plant system. However when we import this configuration to our simulation system, the status of the Phase Server Status (DeltaV) is always BAD. (screenshot below). I am not sure why all those phases are showing up as Bad because on the Production System they are perfectly Ok. I have imported other databases and I had the same issue. I have created brand new databases and still the same problem. All the phases have been verified and have no errors. I am not sure whether DeltaV V14.3 Standalone Simulate allows to run and simulate Recipe. Initially I thought it could be licensing issue however on license verification, it says "OK" for current configuration.
Procedure we followed
FYI: I also created a 14.3.1 system. There is no difference, still get the same issue.
Edit following answer/solution:
In the ProPlus, open the D:\DeltaV\DVData\Download\USERT.scr file in Notepad. Check if DVBATCHADMIN account is present. If the account is present, check if the user is disabled or locked out (in Computer Manager>Local Users and Groups if in a workgroup, Active Directory Users and Computers if in a domain).
If it is missing, perform the following:
In reply to Fariborz: