Was hoping to get some insight into diagnosis and troubleshooting of a signal error I am seeing. I have a (calibrated) Rosemount 1151 wired to an AI 4-20mA HART CHARM.
With the instrument at 4.0mA output, I am seeing a 0.5% (4.08mA) at the AI. With the instrument at 20mA, I see 102.2% (20.35mA) at the AI in DeltaV.
This behavior has been duplicated by removing the instrument from the loop, and sourcing 4/20 from TREX.
Here is a screenshot of the CHARM in Diagnostics with the Instrument at 4.0 mA:
Andre Dicaire
In reply to Andre Dicaire:
Hello Andre Thank you for the prompt response. I will do both: Replace the CHARM and re-test, and I have just logged a CTS with Guardian. I will report back after re-testing the replacement CHARM. Best Regards,
Sim