Previous Control Modules are uploaded to the controller

Dear all,

I am having an issue, whenever i download my professional plus station i get the old control modules back in the controller that i don't want to have. I have deleted these control modules but whenever i do make a complete controller download i get them back. Do it have to do something with the yellow pages? Is there a way to disable the yellow page update.

Thanks and Regards

ASIM

1 Reply

  • Have you followed this procedure:

    1. Unassign the module from the controller.

    2. Select to Delete the module from the controller (right click the module name under the controller and instead of download you get delete from controller)

    3. Select to Delete the module from the database.

    Yellow pages does not control module assignment, execution, or existence.