1) If Selection = Heater B then this expression write target mode: Auto to FF-AO block (PV001A) and CAS to FF-AO block (PV001B). But FF-AO (PV001B) not changing to CAS, means it stays in AUTO mode.
2) If Selection = Heater A then this expression write target mode: Auto to FF-AO block (PV001B) and CAS to FF-AO block (PV001A). But FF-AO (PV001A) not changing to CAS, means it stays in AUTO mode.
Note: If we do manually change of mode of individual FF-AO block its moves from Auto to CAS and vice versa.
Please send your feedback or any resolution on this issue or do we have any hotfixes for this issue.
Andre Dicaire
In addition to what Andre stated there are some other issues in play here. You can't constantly write to a fieldbus device parameters from an expression every scan and should only do a direct write if it is required (at least in the past...more later). Which means you need to put checks if the value that will be written is different than the value that is there before actually writing. Constantly writing has been known to burn up memory in the devices and then stops communicating entirely. Unsure if this has been hot-fixed as I haven't done Fieldbus since Charms was released a "few" years ago but I doubt it has. You also are writing the BKCAL_IN.CV to the BKCAL_OUT.ST after you set using the .CV on the line above, second set should be using .ST instead of .CV.
Agree with Andre that a Splitter might be the best option here. Otherwise you will have to mess with the proper status passing and possibly extra acknowledges logic based on mode changes by operator. If you do go this route I would suggest using a single CALC block and then pass the appropriate values and statuses based on the selection instead of the NOT, ACT and 3 XFR blocks because XFR passes worst status of Selected input and the selector and not just the selected input. Not sure why are you setting the mode of the AO block at all? If in AUTO that means an operator could change the output of non-selected AO which might mess up your control scheme. If the selected Loop goes to AUTO then the proper status needs to be passed back so the Master Loop goes to IMAN and doesn't continue to attempt control. I threw together quickly the below that might get it close (no testing...) if you don't go with the Splitter block but you may have to put other logic for switching between the selection. This also doesn't do anything with Mode or writing SP so you don't have to put all the extra logic in but if you want to do that this logic will get more complicated.
In reply to Matt Stoner: