I would like to setup AO control module without AUTO option. So the AO control module will have only MAN and CAS selection. Is there any issue when it goes from CAS to MAN? This helps us to simply operator training.
Just curious, is this AO for a conventional 4-20 mA output or fieldbus? The old DVC5000 would allow only OOS and CAS enabled (the way we configured AO's by default, before class based modules) and all other modes disabled. As we started upgrading DVC5000's to 6000's, we found we had to leave all modes enabled. A second question: Is it conceivable to simply not expose AO blocks' mode for operator manipulation?